Can You Solve This?
Posted: Sun Jan 01, 2023 4:48 pm
by admin
Greetings Fast Trax® Fam-
Let's assume a 4000 Amp Service. You are being told to supply this service with (10) sets of 600 kcmil CU. What is the size of your GEC to your grounding electrode?
OK....Let's Go!!!!
Re: Can You Solve This?
Posted: Sat Jan 07, 2023 1:33 am
by Ernesto
Ok i will say the GEC should be 2/0 copper. NEC 2020 Table 250.66
Re: Can You Solve This?
Posted: Sat Jan 07, 2023 1:07 pm
by admin
Greetings Ernesto,
No, 2/0 CU is not the answer. Remember it's (10) sets of 600 kcmil you are working with.
Re: Can You Solve This?
Posted: Mon Jan 09, 2023 7:41 pm
by admin
Ok, since it is abundantly clear folks are not enthused about using these new message boards. I thought folks would LOVE the opportunity to post and learn but I guess the generation of today is just not engaging enough. As a result I will go ahead and answer the question.
(10) Sets of really mean nothing in this question. Since we are sizing the GEC (Grounding Electrode Conductor) and didn't say what type of electrode it is, you would logically turn to Table 250.66 for the answer and no math needed. Well, just a little math.
(10) Sets of 600kcmil is 600,000 cmils x 10 = 6,000,000 cmils and that is clearly greater than the 1100 given in the T250.66. So, the GEC never has to be larger than a 3/0 CU or 250 kcmil AL.
Keep in mind that if we had said "ground rods" then you would have simply gone to 250.66(A) and chose 6 AWG CU or 4 AWG AL and move on. But as you know I didn't give you a electrode type so you always default to Table 250.66
You're Welcome!
Re: Can You Solve This?
Posted: Tue Jan 10, 2023 12:24 am
by Ernesto
Thank you so much for the infromation.
Re: Can You Solve This?
Posted: Thu Aug 31, 2023 11:11 am
by brian0104
Thanks again Paul!